Discussion:
Yale ERC050 code #41 SX controller, need parameters.

The dealer can not get me the OEM paarameters for this machine as his info for this serial # says the unit comes with an EV100. It's a GE SX controller and I know that some of the parameters can cause the overheating of this unit and shuting it down with code #41. Model # ERC050RGN48TE082 Ser# E108V18271A. Customer says the Enersys rep checked the battery and it was good BUT I don't like the fact that he is equalizing the charge every other day. I can smell the dust starting to get hot from the drive motor just before the code shows.
  • Posted 5 Sep 2007 16:35
  • By buddy_w
  • joined 1 Sep'07 - 9 messages
  • British Columbia, Canada
Showing items 1 - 5 of 5 results.
I checked the other possibilities as you stated Justin. Same "actuator" since machine was new 4 years ago. Started this problem after the dash display was replaced, which is why I suspected wrong parameters. I think these units have an issue with the displays not lasting? I see Flight Systems has an exchange program on these.
Thanks again.
  • Posted 22 Sep 2007 16:07
  • By buddy_w
  • joined 1 Sep'07 - 9 messages
  • British Columbia, Canada
Thanks guys. The dealer came thru with the proper parameters. Function #8 was way out on the SP/SR controller which set the field current. Now everything works like new. Turns out someone had inadvertantly adjusted the parameters wrong and didn't double check them. Customer was ready to trade in his Yale as he could only use it for 2 hours. Good thing he had a cooler to park it in for a half hour a couple times a day.
Isn't an equalize charge a HIGH rate of charging to bring all the cell gravities up to the same? I have heard of both varients so which one is the truth? Also what is the difference between the GE SP/SR and the SX controllers if any?
Buddy
  • Posted 22 Sep 2007 15:59
  • By buddy_w
  • joined 1 Sep'07 - 9 messages
  • British Columbia, Canada
you have to rule out the "steering wheel actuator" in cases like this

Dang I like that
  • Posted 21 Sep 2007 10:00
  • By proshadetree
  • joined 23 Feb'06 - 484 messages
  • Tennessee, United States
equalize is a slow charge (about 36 hours i believe) if he uses it everyday its probably not fully charged running the equalize every other day
running the battery with a crap charge can heat components
have him change his charging habits

equalize should be run once a month on a light duty shift
batteries should be used for a single 8 hour shift then charged 8 hours then allowed to cool an additional 8 hours
if he is running multiple shifts on a single charge or charging it several times a day (lunch breaks etc) that could cause this
also pushing (bulldozing) pallets along the ground can overheat the machine

you have to rule out the "steering wheel actuator" in cases like this
lol
  • Posted 21 Sep 2007 09:53
  • By justinm
  • joined 13 Apr'06 - 604 messages
  • New York, United States
New York, New York its a heluva town..you know that The Bronx is up..and I'm Brooklyn down
Hello,

I think I have the adjustments you need.
Send me a mail with the volt's off the battery.

[email address removed]

Cheers
  • Posted 8 Sep 2007 23:53
  • By blackie
  • joined 9 Jul'06 - 52 messages
  • Gelderland, Netherlands

Post your Reply

Forkliftaction accepts no responsibility for forum content and requires forum participants to adhere to our rules of conduct. Click here for more information.

If you are having trouble using the Discussion Forums, please contact us for help.

Global Industry News
edition #1260 - 11 December 2025
In this week’s Forkliftaction News we report on DHL Supply Chain signing a deal to deploy autonomous mobile robots (AMRs) at its Mexican retail operations and look at Guidance Automation’s successful trial of an AMR with a hydrogen fuel cell... Continue reading
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY
Movers & Shakers
Jett Chitanand Jett Chitanand
President EPG Americas, Ehrhardt Partner Group (EPG)
CEO, Duravant
Manager of automated solutions engineering and implementation, MHS Lift
President and CEO, Manitou Group
Enforcer FLBAXT25
Braeside, Melbourne, Victoria, Australia
Hire
SMV (Konecranes) 4531CC5
Balling, Denmark
Used - Sale

Showcased in the Virtual Expo

Latest job alerts …
Dayton, OH, United States
Erie, PA, United States