Please help! I have purchased a 2000 Skyjack 3219 that has been sitting outside for years and am stumped. It does nothing, nothing.
4 brand new 6- volt batteries- all load tested
24+ volts at the solenoid
24+ volts at the hydraulic motor
Have bypassed the joystick control cable that goes to the platform and have a known working controller hooked in at the bottom back of the lift
Ground controls don't work
Joystick controls don't work, battery and horn not working
Have tapped on all the small cube relays
Any suggestions on the next troubleshooting tip(s) would be greatly appreciated.
Showing items 1 - 7 of 7 results.
Hey Justin! What's your problem? Make and model?
Did you find a solution yet?
Manuals and technical information on their website.
techpub dot skyjack dot com slash home
might be helpful.
Did you find the problem? I have a similar issue on a 98 boom lift. I am looking for a tech to fix mine for me.
Thanks guys! I will continue the troubleshooting process as recommended.
All controls inoperative?
from the troubleshooting page starting at item #6
(you can download this manual as was suggested in previous post)
make sure you get the correct serial number range of your unit though.
I took a guess but these are the most likely issues causing your problem.
6. Fuse F1 defective.
- Replace fuse.
7. Main battery disconnect switch S1 open or defective.
- Close switch. Check continuity. Replace if defective.
8. Loose or broken wire #3 from motor contactor C1 to circuit breaker CB2.
- Check continuity. Replace if defective.
9. Loose or broken wire #3A from circuit breaker CB2 to charger relay L1CR.
- Check continuity. Replace if defective.
10. Defective or tripped circuit breaker CB2.
- Reset circuit breaker. Replace if defective.
11. Defective battery charger relay L1CR.
- Check relay. Replace if defective.
12. Loose or broken wire #5 from charger relay L1CR to base emergency stop switch S28.
- Check continuity. Replace if defective.
13. Open or defective base emergency stop switch S28.
- Close switch. Check switch. Replace if defective.
14. Loose or broken wire #5A from base emergency stop switch S28 to base key switch S10.
- Check continuity. Replace if defective.
15. Open or defective base key switch S10.
- Select function with switch. Check switch. Replace if defective.
16. Loose or broken wire #00 from pump motor DCM1 to circuit breaker CB1.
- Check continuity. Replace if defective.
17. Defective or tripped circuit breaker CB1.
- Reset circuit breaker. Replace if defective.
18. Loose or broken wire #02 from circuit breaker CB1 to base terminal block.
- Check continuity. Replace if defective.
19. Loose or broken wire #7A from base terminal block to CM1 control module pin P2-12. (CE)
- Check continuity. Replace if defective.
20. Loose or broken wire #02 from base terminal block to CM1 control module pin P2-11. (CE)
- Check continuity. Replace if defective.
I would be checking the emergency stop buttons to make sure they are not staying on....also would check all connections for corrosion.....check the key switch also......you can go to skyjacks website and view and print the service manual with wiring diagrams and also the troubleshooting for your lift.....