Symptom
Forward or reverse contactors open and close, then can
only be closed by opening and closing the key switch.

Possible Causes
Reversed yellow and green current senors wires
- Insure that the:
- green wire connects to PZ4 with
no open circuits.
- yellow wire connects to PZ3 with
no open circuits or loose connections

Reversed power cable connection.
- Insure that the battery negative cable connects to
SCR NEG and the motor A2 cable connects to SCR
A2

I'm sure you have already checked this?
  • Posted 26 Mar 2014 23:17
  • By swoop223
  • joined 23 Mar'12 - 3,692 messages
  • North Carolina, United States
You've been swooped!
swoop223@gmail.com

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY
Fact of the week
According to studies published in the English Journal of Medicine, the impact of daylight savings is revealed by a 24% increase in heart attacks on the Monday following the spring shift forward. When clocks move back in autumn, heart attacks drop by about 21%, suggesting that loss of sleep is an important driver.