yes, almost anything can cause this. this is a safe start up protection, (we call it it SRO*) and if _anything_ is not just right, then you don't want to risk getting a "run away" condition.
If I had to take care of that many of these, I sure would expect whom ever owned them to provide a GE handset, if I didn't have one of my own.
the dash, and or the handset should give you some error codes when this unit does not start correctly, and the first 8 or so just have to do with correct order of start-up (you need to be in neutral when the key turns on, or go through neutral so the control sees the correct signals)
SRO= Static return to off. if the control does not see the correct signals of 0 vdc, it turns off until it does see the correct signals. the potentiometer being 'at rest' and adjusted to register the reading it has as 'at rest' with the controller are also SRO requirements.
  • Posted 4 Jul 2013 00:08
  • By edward_t
  • joined 5 Mar'08 - 2,334 messages
  • South Carolina, United States
"it's not rocket surgery"

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Load Lifter 2414-8G
Flesherton, Ontario, Canada
New - Sale
TCM FD115-3
Yokohama, Japan
Used - Sale

PREMIUM business

Zhejiang UN Forklift Co., Ltd
Manufacturer of IC forklifts, electric forklifts and warehouse equipment.
Upcoming in the editorial calendar
MANAGING MIXED FLEETS
Oct 2025
ASSET FINANCE
Nov 2025
Fact of the week
At the opening ceremony of the Sydney Harbour Bridge in 1932, marching bands were instructed to walk out of step as they crossed the bridge. This unusual directive was given as a precaution due to concerns about the bridge's structural integrity during its early use.