This is for a EV100LX. I hope this helps.

This status code is displayed when the voltage at T2 is less than 12% of battery
volts during the look ahead test.
Symptom: Forward or reverse contactor will not energize.
Possible Cause
- Defective forward or reverse contactor.
* Check for welded forward or reverse contact tips.
* Check condition of forward and reverse contactors. Sluggish operation will cause this status code.
- Defective 3 REC circuit.
* Check for shorted 3 REC.
* Check for shorted 3 REC snubber (23 REC).