Showing items 1 - 3 of 3 results.
20.60 S Pressure feed-back line is indicating there is no
system pressure present, allthough pressure should
be there
Controller reverts to a "shut down" mode and will force neutral
0
Stop machine & Contact maintenance for troubleshooting The analog input ANI0 is in the 1500 - 4000 ohm
range, while it should be in the 500 - 1500 ohm
range
Check the wiring between the controller and the pressure feedback sensor. Check
the pressure feedback sensor (engine running / stopped).
Hi, i have codes t2060 and t_sht. I need a list of fault codes.
Shut-Down Mode is activated if serious internal or external fault is detected.
When the mode is activated, the transmission will be automatically
set to neutral as the redundant shut-down circuit cuts hydraulic
pressure to the connection. This mode is only selected if nontolerable faults occur.
U have to check what's error it is. Press M when there is error and check the Err, should be four numbers.
Turning off machine erase errors.
It might be pressure feedback sensore or one of the RPM sensors