Code -65

Serial number A3EC 340953. Started with code -51. Found burnt lugs on SX controller, replaced controller. Now I get code -65. Checked and replaced line contactor. No help. What else can cause this code?
  • Posted 11 Jun 2015 11:52
  • By Semperfiguy98
  • joined 19 Sep'12 - 21 messages
  • California, United States
Showing items 1 - 3 of 3 results.
Do you have a GE handset?
if so get the correct cable with the connector that connects to the SX controller and go in and check the settings.

you may want to check the settings in the controller, these are what they should be for this model, ONLY THIS MODEL:
Function: 36v 48v
1 16 16
2 60 60
3 20 27
4 255 255
5 15 15
6
7 80 80
8 255 255
9 35 35
10 255 255
11 0 0
12 0 0
13 113 113
14 24 16
15 36 48
16 130 130
17 135 135
18 149 149
19 255 255
20 255 255
21 30 25
22 183 183
23 50 50
24 100 100
25 0 0
26 5 5
27 0 0
28 0 0
29 0 0
30 0 0
48 30 40
49 0 0
50 0 0
51 80 80
52 30 40
53 18 18
54 0 0
55 0 0
56 20 27
57 35 35
58 30 25
59 0 0
60 15 20
61 70 70
62 60 50
63 0 0

make sure it is set this way.

and please go back and double check your wiring to the line contactor, trace these wires to their origins or destinations and make sure there are no pinched or chaffed wires that could be shorting somewhere on the frame.
  • Posted 20 Jun 2015 05:32
  • By swoop223
  • joined 23 Mar'12 - 3,696 messages
  • North Carolina, United States
You've been swooped!
swoop223@gmail.com
I replaced the contactor and PTC. I also swapped controllers with a known good one. The wiring hasn't changed since it ran. It still has code 65. This is a difficult one to troubleshoot.
  • Posted 20 Jun 2015 03:19
  • By Semperfiguy98
  • joined 19 Sep'12 - 21 messages
  • California, United States
could be a bad PTC across the line contactor buss (that's the flat capacitor looking device that hooks between the buss bar connections on the line contactor, about the size of a quarter)
may be open, could have a bad connection.

also welded 1A contactor can cause this (if equipt with one)

check for continuity across the open 1A contactor

possible wiring error, insure no device is connected to the load side of the line contactor

worse case scenario is a bad controller unit
  • Posted 11 Jun 2015 14:42
  • By swoop223
  • joined 23 Mar'12 - 3,696 messages
  • North Carolina, United States
You've been swooped!
swoop223@gmail.com

Post your Reply

Forkliftaction accepts no responsibility for forum content and requires forum participants to adhere to our rules of conduct. Click here for more information.

If you are having trouble using the Discussion Forums, please contact us for help.

Fact of the week
Foundling hatches are safe, anonymous drop-off points for unwanted infants, allowing parents in crisis a way to surrender a baby safely without fear of punishment, ensuring the child is rescued and cared for. The concept started in the 12th century, was abandoned in the late 19th century, then reintroduced in 1952. It has since been adopted in many countries.
Winners of 7th LEEA Awards named Liverpool, United Kingdom

PREMIUM business

VETTER Forks, Inc.
The world's most comprehensive product range as well as the most intelligent sensor fork for more safety and efficiency.
Movers & Shakers
Jett Chitanand Jett Chitanand
President EPG Americas, Ehrhardt Partner Group (EPG)
CEO, Duravant
Manager of automated solutions engineering and implementation, MHS Lift
President and CEO, Manitou Group
Winners of 7th LEEA Awards named Liverpool, United Kingdom
Upcoming industry events …
January 28-30, 2026 - Bangkok, Thailand
March 4-5, 2026 - Detroit, Michigan, United States
March 24-26, 2026 - Stuttgart, Germany
Movers & Shakers
Jett Chitanand Jett Chitanand
President EPG Americas, Ehrhardt Partner Group (EPG)
CEO, Duravant
Manager of automated solutions engineering and implementation, MHS Lift
President and CEO, Manitou Group