Error code 29 - Main contactor fault

Indicates ED (main) contactor is open or short

Verify buss bar and power connections at ED contactor and traction controller.

Verify ED t contactor tips are not welded or obstructed.

Disconnect wires from ED contactor and test resistance of coil, if less than 48 or greater than 65 ohms, replace contactor. If between 48 & 65 ohms, replace traction controller.

I'd be hesitant about replacing traction controller without being as sure as possible that it was faulty.

There should be a diode or suppressor across the ed contactor, disconnect one end of it before testing resistance. Also test it for short or open circuit. Also check fuses next to ed contactor (remove them and test)
  • Posted 11 Mar 2015 08:30
  • By techno_nz
  • joined 9 Aug'13 - 138 messages
  • Canterbury, New Zealand

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY
Movers & Shakers
Jett Chitanand Jett Chitanand
President EPG Americas, Ehrhardt Partner Group (EPG)
CEO, Duravant
Manager of automated solutions engineering and implementation, MHS Lift
President and CEO, Manitou Group

Showcased in the Virtual Expo

Fact of the week
Foundling hatches are safe, anonymous drop-off points for unwanted infants, allowing parents in crisis a way to surrender a baby safely without fear of punishment, ensuring the child is rescued and cared for. The concept started in the 12th century, was abandoned in the late 19th century, then reintroduced in 1952. It has since been adopted in many countries.