Hate to say it but the control voltage is not correct.
GE does not make a 12v system in the EV100 controllers.
Your control voltage should be battery volts which should be either 24 or 36v, which ever battery and controller it has in it.
If you are getting only 13v at the coil supply wire you have a problem and need to backprobe the system till you find where the voltage loss is coming from.
  • Posted 16 Dec 2014 06:39
  • By swoop223
  • joined 23 Mar'12 - 3,696 messages
  • North Carolina, United States
You've been swooped!
swoop223@gmail.com

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Fact of the week
Foundling hatches are safe, anonymous drop-off points for unwanted infants, allowing parents in crisis a way to surrender a baby safely without fear of punishment, ensuring the child is rescued and cared for. The concept started in the 12th century, was abandoned in the late 19th century, then reintroduced in 1952. It has since been adopted in many countries.
Fact of the week
Foundling hatches are safe, anonymous drop-off points for unwanted infants, allowing parents in crisis a way to surrender a baby safely without fear of punishment, ensuring the child is rescued and cared for. The concept started in the 12th century, was abandoned in the late 19th century, then reintroduced in 1952. It has since been adopted in many countries.