PDF SBR switch is related to the battery-door switch.

NC switch on right side of machine on battery-door.
To prevent driving when battery-door is openend.
Very often the wiring of this switch is getting between door and chassis, resulting in broken wiring.

For testing purpose, just remove switch, connect the 2 wires so master will see this as a NC contact.
If unsuccesfull, wiring is broken.

Connection on pumpcontroller E12, wire 68 switches to E4 common wire 222 (A trough E)

Good luck!
  • Posted 28 Dec 2018 19:19
  • By Speedfreak
  • joined 24 May'18 - 103 messages
  • Niederlande, Netherlands

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY
Fact of the week
The two internal cavities in our nose called nostrils function as separate organs. Each nostril has its own set of turbinates and olfactory receptors. The two independent organs work together through a mechanism called the nasal cycle, where one nostril is dominant for air intake while the other rests and is better at detecting scents.