OM/Komatsu Reach throttle error

HI there
We have a customer with a OM pimesbo/Komatsu reach FB20RW1R/C1/PKKL
serial: F24519R0025

The original controller was damaged due to water ingress. The customer replaced the controller which when powered up came with error 'pot out of range'. Unfortunately the pot will not calibrate. The customer has tried with the pimesbo software, the win zapi software and even the komatsu/Zapi analyser.

They have also changed the full controller as they suspectedit might be a problem in the controller. Still the same error.
They then tried changing the foot pedal, which still comes up with pot out of range error and still will not allow calibration.

When testing the foot pedal on the handset it shows it changes from 0.3v up to 5v, but when they go into calibration mode, nothing changes the values all remain on 0.00v.

All the wires check back from the foot pedal to the unit ok also.

Any pointers would be of great help.

Regards
  • Posted 9 Dec 2013 22:11
  • By elektrodrive
  • joined 2 May'08 - 743 messages
  • West Midlands, United Kingdom
enquiries@elektrodrive.co.uk

http://www.facebook.com/pages/Elektrodrive/135894223166624
Showing items 1 - 5 of 5 results.
update:
it was the hydraulic lever pots faulty which was also preventing throttle calibration. once these were replaced it now allows calibration.

Thank you for all the assistance.
  • Posted 11 Dec 2013 20:44
  • By elektrodrive
  • joined 2 May'08 - 743 messages
  • West Midlands, United Kingdom
Sorry the error was 'put out of range'.
Which according to the manual is related to hydraulic.
  • Posted 10 Dec 2013 07:15
  • By elektrodrive
  • joined 2 May'08 - 743 messages
  • West Midlands, United Kingdom
enquiries@elektrodrive.co.uk

http://www.facebook.com/pages/Elektrodrive/135894223166624
Thank you for your comments and the information you have supplied. I was looking at the error list and it appears it could be pot out ofc range error related to the hydraulic lever pots and not the accelerator pot as I initially thought.

it also would not let me calibrate hydraulic.

we will try again this time focusing our attention on the hydraulic levers.

Will update once resolved.

Thanks once again
  • Posted 10 Dec 2013 07:12
  • By elektrodrive
  • joined 2 May'08 - 743 messages
  • West Midlands, United Kingdom
enquiries@elektrodrive.co.uk

http://www.facebook.com/pages/Elektrodrive/135894223166624
If you can see that value from pedal on test min position MUST BE 0.5V and max is 5V
Please record like that it must to work
Are you sure that is drive pedal,what error you have on start up
  • Posted 10 Dec 2013 05:19
  • Modified 10 Dec 2013 05:32 by poster
  • By nemanja_k
  • joined 15 Apr'11 - 398 messages
  • serbia, Serbia
Hmm.. strange thing,

The communication between the analyser/pc-- truck is Ok?, did you try first to teach in the hydraulics pots??

Check mail

Regards
  • Posted 10 Dec 2013 05:11
  • By nacsand_n
  • joined 20 Sep'09 - 716 messages
  • Madrid, Spain

Post your Reply

Forkliftaction accepts no responsibility for forum content and requires forum participants to adhere to our rules of conduct. Click here for more information.

If you are having trouble using the Discussion Forums, please contact us for help.

Toyota launches three new stackers Columbus, IN, United States
Bobcat appoints new UK dealer Liverpool, United Kingdom
Mitsubishi FGE35AT
Yokohama, Japan
Used - Sale
UN Forklift FB25N1LZ1
HANGZHOU, Zhejiang, China
New - Sale
Global Industry News
edition #1244 - 21 August 2025
In our feel good story for the week, we report on a donation from Wisconsin-headquartered Big Forklifts to the University of Wisconsin-Madison’s College of Engineering, after discovering the institution was still using one of its 1960s walkie stackers... Continue reading
Fact of the week
Portugal was the first country to implement a nationwide, automatic electronic toll collection system. This system allows vehicles to pass through toll booths without stopping, significantly improving traffic flow on highways.