the EP108 is the controller version software i'm pretty sure

As for the alarm code
AL60 is:
NO Field Current (LED on controller will flash 6 flashes)

Possible causes:
- Open F1 or F2 fuse
- Cable connection to motor fields loose or open
- Motor field winding is open or too high (should measure less that 2ohms)
- Main contactor circuit damaged or disconnected
- Check contactor coil (should read 45 to 55ohms resistance)
- Failure of current sensor or field current driver (inside controller)
- Check for resistance between A1 and A2 to case, it should have approximately 0.5 mega ohms.
- Check relay

Hope this helps