Toyota FBEU18 codes AD-1 and -2.....

Traveling AC driver 1 + main controller communication abnormality
Condition for detection: Output when the CPU board cannot receive ID code from the traveling AC driver 1 upon key switch on.

Check CN103, CN104, CN110 and + CN112 connection condition Harness check (Especially No. 42 line.)

Check the continuity of communication line harness.
CN103-1(145) CN110-3(145)
CN103-l(145) CN112-l(145)
CN 103-2(146) CN110-4(146)
CN 103-2(146) CN112-2(146)
CN103-3(147) CN110-6(147)

No Continuity then harness is defective


If there is continuity then Traveling AC driver 1 defect (There is possibility that CPU board is defect.)
  • Posted 11 Nov 2017 11:24
  • By kevin_t
  • joined 2 Dec'10 - 1,301 messages
  • Pennsylvania, United States

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Manitou M50-4
Braeside, Melbourne, Victoria, Australia
Hire
Crown RD572513TT6860R
Braeside, Melbourne, Victoria, Australia
Hire
Global Industry News
edition #1236 - 26 June 2025
As June comes to a close, the month when our sector recognises National Forklift Safety Day , the United Kingdom’s Association of Industrial Truck Trainers (AITT) has issued a timely reminder of the need to ensure any staff training is fully accredited... Continue reading
Fact of the week
Sourdough bread contains Lactobacillus reuteri, a probiotic bacteria. During pregnancy and breastfeeding, these bacteria can travel from the mother's colon to her breast tissue and be passed to the infant through breast milk. It offers various health benefits, including potential protection against breast cancer.

Showcased in the Virtual Expo

Upcoming in the editorial calendar
WIRELESS CHARGING
Aug 2025
MANAGING MIXED FLEETS
Oct 2025