I would check the voltage at the contactor continuously until it cuts out. Does it drop slowly? Also check all cables and wires for good connection.

Code E107 - Contactor Off
-Reason-
Contactor probably present but controller could not close it successfully.
-Possible Cause/ Corrective Action-
Problem with main contactor tips.
* If contactor clicks prior to displaying this code, polish contactor tips. If
this is unsuccessful, replace contactor.
Low voltage.
* Try closing contactor with a known-good battery.
Short in contactor coil wiring.
* Replace contactor.
  • Posted 11 Oct 2024 06:59
  • By lumberjack
  • joined 27 Jul'07 - 183 messages
  • Maryland, United States

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Fact of the week
Brothers Adolf ("Adi") and Rudolf ("Rudi") Dassler split their shoe company after WWII due to a bitter feud, and established the rival companies of Adidas and Puma. Their personal animosity and business rivalry divided their German hometown Herzogenaurach. The town became known as "the town of bent necks" due to the intense loyalty to each brand.
Terberg RT403
Balling, Denmark
Used - Sale
Terberg RT223
Balling, Denmark
Used - Sale
Upcoming industry events …
October 14-16, 2025 - Antwerp, Austria
October 15-17, 2025 - Bangkok, Thailand
November 17-19, 2026 - Luanda, Angola
Fact of the week
Brothers Adolf ("Adi") and Rudolf ("Rudi") Dassler split their shoe company after WWII due to a bitter feud, and established the rival companies of Adidas and Puma. Their personal animosity and business rivalry divided their German hometown Herzogenaurach. The town became known as "the town of bent necks" due to the intense loyalty to each brand.