The control system must provide a Run/Stop switch or a key switch to control engine start and stop.
The Run/Stop switch must be independently controlled from the ECM power supply;
The engine stop is realized by the Open/Stop switch open circuit, and the ECM power supply can be removed/closed after 30s of shutdown.
After the Run/Stop switch is turned off, it still takes a little time to process the data and save it (similar to the computer shutdown process). If the ECM power is removed/closed prematurely, the fault codes SPN627 and FMI2 will appear.
ECM lines must be installed in accordance with the circuit diagram
Any device capable of generating an induced electromotive force must be installed with a back EMF suppression coil connected to the ECM;
All welding work must be carried out after all ECM connectors have been disconnected. Welding will damage the ECM.

If you want to know more, please get help from support: https://www.dieselgeneratortech.com/support/
  • Posted 7 May 2019 19:08
  • By Ange_ou
  • joined 7 Jun'18 - 2 messages
  • Jiangsu, China

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Global Industry News
edition #1235 - 19 June 2025
Greek philosopher Heraclitus is credited with the famous saying “change is the only constant”, and this week’s Forkliftaction News demonstrates this is certainly true in the case of the materials handling sector... Continue reading
Fact of the week
Bluetooth is named after the 10th-century Viking king, Harald Bluetooth, who united warring tribes in Denmark and Norway. In 1997, Jim Kardach from Intel gave the name to the technology because of its ability to unite different communication protocols, just as Harald united various tribes.
Upcoming industry events …
July 22-24, 2025 - Sydney, Australia
November 11-13, 2025 - Singapore, Singapore
November 12-13, 2025 - London, United Kingdom