ev-100 system
Status Code -48
Description
Voltage check at T2 is greater than 88% of battery voltage.
Cause of Status Indication
This Status Code will be indicated when a voltage check at T2 is greater than 88% of battery voltage.
Memory Recall
No
Circuit
Traction
Indication of Fault
Line Contactor L will not close. Forward or Reverse contactors will not close.
Possible Cause
Malfunction of Forward or Reverse contactors.
Check for welded contacts that hold a Forward or Reverse contactor closed.
Check for slow operation of a Forward or Reverse contactor.
Malfunction of diode D3 circuit. Check for a short circuit across D3.
Check for a short circuit across the suppressor for D3.


SEM Systom
Maximum travel speed is reduced or lift truck does not move.

Possible Causes and Test Procedures
* If the fault code is intermittent, verify that the accelerator potentiometer is adjusted correctly.
Adjust the accelerator potentiometer.
* Check for open motor field coils or loose or intermittent field connections, or open F1 or F2 connections.
Repair loose or open connections.
  • Posted 8 Aug 2017 14:33
  • By glock01
  • joined 26 Apr'09 - 19 messages
  • Idaho, United States

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
TCM FHD105Z
Yokohama, Japan
Used - Sale
Toyota 8FG25
Braeside, Melbourne, Victoria, Australia
Hire
Upcoming industry events …
September 24-25, 2025 - Tangiers, Morocco
September 25, 2025 - South Brisbane, QLD, Australia
October 23, 2025 - Atlanta, GA, United States
Fact of the week
At the opening ceremony of the Sydney Harbour Bridge in 1932, marching bands were instructed to walk out of step as they crossed the bridge. This unusual directive was given as a precaution due to concerns about the bridge's structural integrity during its early use.
Global Industry News
edition #1247 - 11 September 2025
In what may prove to be a sign of things to come, Canadian materials handling equipment lithium-ion battery manufacturer, UgoWork, has announced battery assembly for some forklifts bound for the North American domestic market will now be done in the US. See the story for full details... Continue reading

Showcased in the Virtual Expo

Fact of the week
At the opening ceremony of the Sydney Harbour Bridge in 1932, marching bands were instructed to walk out of step as they crossed the bridge. This unusual directive was given as a precaution due to concerns about the bridge's structural integrity during its early use.