TCM FG25T3:
Accelerator calibration

Replaced the potentiometer on the accelerator is there a way to calibrate it?
  • Posted 19 Nov 2024 07:14
  • Discussion started by Harley_Gwyn
  • Texas, United States
Harley
Showing items 1 - 1 of 1 results.
This is the procedure from the manual.

1. Monitor APS1 (Green/Red Pin 5) and APS2 (Green/White Pin 2) voltages.

2. Adjust sensor mounting angle so that APS1 output is 0.67v to 0.87v when accelerator is fully released and then tighten the sensor mounting bolt.

3. Under the condition of step 2, APS2 output is within 0.33v to 0.43v.

4. Make sure the accelerator fully depressed stroke is within specified range.

5. With the accelerator fully depressed make sure APS1 output is within 4.4v to 4.6v.

6. Double check accelerator released APS1 output is 0.67v to 0.87v.
  • Posted 19 Nov 2024 08:00
  • Reply by BLey
  • Ontario, Canada

Post your Reply

Forkliftaction.com accepts no responsibility for forum content and requires forum participants to adhere to the rules. Click here for more information.

Having trouble using the Discussion Forums? Contact us for help.

Global Industry News
edition #1228 - 1 May 2025
There is simply no ignoring the push for a greener, more sustainable materials handling equipment industry as manufacturers and customers alike seek eco-friendly solutions to reduce or eliminate carbon emissions... Continue reading
Fact of the week
On average, people read 10-30% slower from a screen than from paper.
Fact of the week
On average, people read 10-30% slower from a screen than from paper.
UN Forklift FD40T
HANGZHOU, Zhejiang, China
New - Sale
UN Forklift FB25N1LZ1
HANGZHOU, Zhejiang, China
New - Sale

Showcased in the Virtual Expo

Fact of the week
On average, people read 10-30% slower from a screen than from paper.