FIRST BLOCK THE TRUCK SO THE DRIVE WHEELS ARE OFF THE GROUND!

code 04 description
Start switch input low after initial start up.

Symptom
fwd or rev contactor will not pick-up

Possible cause
fwd or rev directional switch closed on initial start up
Depress accel and see if code 03 or 02 comes up after start up if 03 then the rev switch is closed if 02 comes up the fwd switch is closed.
Possible cause 2
Excessive leakage from TB2 to battery negative
Check voltage at TB2 with key and seat switches closed and directional lever in neutral. voltage should be greater than 60% of battery voltage.

If less than 60% voltage. remove wire from TB2 and measure ohms from wire to terminal N on traction panel. Value should be greater than 22k ohms.

you may have a glitchy switch. this is normally an out of sequence code on start up.
  • Posted 11 Dec 2010 08:52
  • By bruce_c
  • joined 28 Jul'10 - 52 messages
  • Missouri, United States

This is ONLY to be used to report flooding, spam, advertising and problematic (harassing, abusive or crude) posts.

Indicates mandatory field
Fact of the week
The two internal cavities in our nose called nostrils function as separate organs. Each nostril has its own set of turbinates and olfactory receptors. The two independent organs work together through a mechanism called the nasal cycle, where one nostril is dominant for air intake while the other rests and is better at detecting scents.

PREMIUM business

Shenzhen Wellwit Robotics Co., Ltd
The Largest AMR/AGV ODM/OEM Manufacturer in China.
Latest job alerts …
Monmouth, IL, United States
Bensenville, United States
Bensenville, United States
Editorial calendar - planned features
CONSTRUCTION FORKLIFTS
HANDLING GOODS IN THE COLD
LOADING/UNLOADING FREIGHT
BROWNFIELD AUTOMATION
FORKLIFT ATTACHMENTS
BATTERY AFFORDABILITY AND LIFETIME
FORKLIFT SAFETY